Ok folks here it is the Fire Marshals Inspection Report. With help most of this has already been completed or temporarily shut down till we can comply with fire code. Below is a list of exactly what the fire marshals inspection report said with applicable code. He did not list every applicable code just the general code that applies, on most items several codes applied. We have until 30June15 to comply with or begin serious effort to remedy all of these items.
1011.3 Illumination.
**Repair all exit signs so that they are illuminated at all times.
Status-completed by Andrew, William, Lance, and I
1011.1 Where Required.
**Install an illuminated exit sign inside the hands on/interactive classroom.
Status-not necessary after speaking to the marshal however we are going to do it anyway for safety.
2803.2 Dust Control.
**All wood cutting equipment in the wood shop area shall have adequate dust collection devices that shall be maintained.
Status-Complete the ventilation system was maintained by Andrew and the woodshop cleaned by me, now it needs to be maintained.
803.1 General.
**Replace all ceiling tiles throughout space such as in the wood shop.
Status-In Progress after leak repair is complete it will be completed
315.3.3 Equipment Rooms.
**Combustible material shall not be stored in boiler rooms, mechanical rooms or electrical equipment rooms.
Status-Complete my wife and I cleaned it out.
906.3.4 Class D Fire Hazards
**Shall have at least 2 x class D portable fire extinguishers at location in areas where combustible metals will be worked on.
Status-Complete Allen purchased one for the metal shop and we can put this on a roller cart for ease of use and mobility to milling when needed as this was the second area of concern for the marshal. Still recommended we buy a second though.
2404.2 Location spray-finishing operations.
**Spray painting operations at location shall stop immediately and can not be resumed until proper permitted spray booth room have been submitted for review and approved then installed and inspected. The closet currently being used is not appropriate for use as a spray booth or room.
Status-Complete and pending, shutdown and pending real paint booth install.
603.5.2 Heating appliance installation and maintenance.
**The kilns located in warehouse shall not be used until permit is applied for and plans submitted for review and approved. The exhaust shall also be repaired and all components shall meet codes and ordinances as required.
**The current exhaust setup is not adequate and unacceptable.
Status-Complete and pending, shut down and pending re install.
3501.2 Permits.
**Plasma cutter is prohibited from use at this location at this time.
**A permit shall be applied for showing equipment, ventilation, location in building etc.
**Once this is reviewed and if allowed then equipment can be operated under proper operators and with all proper safety checks in place.
Status-Pending, shut down and working on issue
901.6 Inspection, testing and maintenance.
**The smoke detectors, pull stations and notification devices located in this space are not currently wired to the buildings fire alarm panel located in suite #100. These devices shall be wired to and monitored by this fire alarm panel right away. More devices may be required and will be determined upon evaluation with fire alarm company of occupants choice and fire inspector. Until these devices currently at location become active, they shall be covered up so as to not appear to be life safety devices that will not function as designed.
Status-Pending
5003.4 Material Safety Data Sheets.
**All MSDS shall be kept in approved location on site.
**The preferred method is a spreadsheet that has all chemicals listed with their MSDS put into a thumb drive that will be placed in Know Box.
Status-Pending
102.3 Change of use or occupancy.
**Occupant shall reapply for a new Certificate of Occupancy showing all types of work/classes going on at location.
Status-Pending
Issues he brought up off report but will end up on the next inspection 30June15 if not worked on:
-GFCI sockets for anything within 6 ft of water source. Specifically the bio area water tank.
-Brewing is a no go at all, no books no equipment or we meet and permit for brewery or distillery.
-We need to schedule weekly cleanup on the space to ensure it stays clean and safely accessible such as pathways and equipment. Have this posted.
-Look at having laser C02 cans tagged and inspected.
-Check sprinkler heads in metal and workshop to ensure it is correctly rated for the area.
-Get all alarms and fire detectors wired in and connected to fire panel.
-Anything with potential for fire such as kilns and electrical panels and welders need 3ft clearance around it.
-MSDS for Gallon size and up
-Propane external storage meeting Texas Railroad commissions standards suggest at least 5 ft from exit door and in locked cabinet.
-Extension cords not being used as permanent supply lines store them when not in use or possibly get higher rated cords for certain uses
-Mark forging as storage only
-Wood storage should be moved off site, personal small storage not an issue but storing large amounts of lumber not okay. If it catches we donât have the equipment to put it out quick enough.
-Keep milling cleaned up to much mess and risk of metal fire.
-Check and possibly permit laser