Continuing the discussion from Anyone Good at Evacuating Refrigeration Systems?:
Forgive my virtually complete ignorance…
I’ve done A/C work for years, and we just hook up a gauge, pull a vacuum, and look for ~ -29 gauge units (I think it’s PSI). Evacuate at this rate for 15 or so minutes, and then cap off. Check after 1 hour to make sure the gauge has not moved, and if not, charge with refrigerant and get that shyte out the door.
So, on the chart @Photomancer posted, very cool, BTW, the PSI does not go negative. I assume this is because these are “absolute psi” instead of “gauge psi”, wherein the “gauge psi” 14.7 (or so) reads zero. In other words, 1 atmosphere is equal to zero on the average a/c gauge setup. Right? OK.
So, the venturi vacs like the one available in the 'space and, therefore, I assume the one the Science Committee has used, claims to pull 28.3 inches of mercury. I assume that’s “gauge” on the chart, and therefore is roughly 1.57 inches of mercury absolute, or 5.3kPa, or 5300 Pa, or 40,000 Micron. Right?
This is 5.3X10^3, which falls under “medium vacuum” on the Vacuum Ranges chart, right?
So, this pump David’s talking about (lending or donating) is capable of <50 micron, (similar pumps to what I think this is specify 35 microns), which, as is pointed out, is .00065 kPa, which is .65 Pa. Right?
.65 Pa is 6.5X10^-1, which falls under the “High Vacuum” category on the Vacuum Ranges chart, right?
Thank you to anyone who can confirm or correct my assertions. It’s clear I don’t do this stuff enough any more, and that I should pay more attention to the things I do.