Page 10 of the operation manual says a 30Amp breaker is recommended. [EDIT: Correct info - 40A breaker is recommended].
This suggests to me that the manufacturer expects a lot less than 45 amps. Does this mean there’s something wrong with the planer if it’s generating surge current of over 45 amps?
Someone needs to confirm this. While I really hate to keep jerking around the engineer, we need to know this before we actually build …
So the four on the bottom of page 23 all seem plausible, four being least likely. I believe it’s a 3ph I’ll be at space for a tour tomorrow and pop in to check
At 208 volt you are going to see additional current so it would not be uncommon to bump up the current capacity of the breaker to handle the surge current.
Your absolutely right it’s the initial surge current I have graphs of the power consumption if you would ever like to see them but from what I am seeing the breaker as it is can not handle the surge current.
Are those breakers rated for a set number of trips? I’m sure that breaker has been tripped quite a few times, but I don’t know the expected behavior of repeatedly being tripped over time.
At 208 volts that’s 44.23 amps which is pretty close to what Robert said is being observed. Sounds like a new and thicker line needs to be run that’s capable of 50 amps or more. Or wait until the move?