I successfully installed the interlock on the Delta but the initial surge current is hitting approx 30 amp’s where I had my fast act fuse and so I am the cause of the Delta going down. I have new fuses coming in that are slow/time delay fuses which I am hopefull fix the surge current issue. Sorry about the outages and I hope to have it fixed next week with some new fuses. If the new fuses don’t work I will move to a contactor and remove the fuse all together.
What style of fuse are you using?
1/4x1.25 glass fuse.
I have some of these on the way
https://www.mouser.com/datasheet/2/87/BUS_Elx_DS_2002_MDA_Series-335907.pdf
Delta table saw?
Wow, I thought we were only pulling 4-5 amps the other day… hard to believe the starting spike on that motor is that high.
Yes the Delta Table Saw
Motors need a different style fuse than transformers. Simply put a fuse isn’t just a fuse. You can’t put a motor rated fuse into a transformer circuit and not expect issues. Inrush on a motor is more predictable than that of a transformer.
Fuseco is down the street. The after hour opening fee is hard to swallow, 200$. But during the normal working hours are great.
Update: I went ahead and removed the interlock until the new fuses come in. The Delta Saw is back up and running.