Legalities … Per my burg’s ordinances, a backup generator must comply with…
-
UL 2200 : Standard for Stationary Engine Generator Assemblies
- Should be a stock cert on the generator itself
-
NFPA 70 : National Electrical Code
- Should be fine so long as I watch my terminations, use good wiring, and use a compliant transfer switch
-
NFPA 110 : Standard for Emergency and Standby Power Systems
- Seems to concern itself mostly with huge standby generators that spool up automatically that are tightly integrated with a facility
- My installation would be a Class 2 (its failure will have no impact on human or facility life safety) in an outbuilding with no provision for human entry, thus easier to install
- Does not mandate fireproofness nor offsets from the building
-
NFPA 111 : Standard on Stored Electrical Energy Emergency and Standby Power Systems
- Seems to mostly focus on battery banks and UPSs